On Wed, 2008-09-17 at 09:02 -0400, Josh Luthman wrote:
> I don't have Devmon installed and I would, if at all possible, prefer
> to avoid SNMP.
We use Liebert/Emmerson UPS here, (GXT2, NPower, and NFinity) and I
monitor about 130 UPS. I use MRTG, configured with a template, to poll
the boxes. bbmrtg.pl imports the data into hobbit. I am alarmed on:
1. Load on battery
2. UPS switched to Bypass
3. Battery less than 60 minutes (yellow) or 30 minutes (red)
4. Current draw within 10% of rated max
5. Input voltage more than 15% below nominal (brown-out) or 15% above
nominal.
6. frequency off by more than 1Hz
7. UPS inaccessible (ping)
I can't fathom a way to monitor that without snmp.
--