[hobbit] NCV Graph not showing up
Maxeiner, Christian
christian.maxeiner at usd.de
Wed Apr 26 09:48:34 CEST 2006
I tried that without success. Anyway this makes no sense because the
test name is "roomtemp", "Temperature" is just the value.
My RRD-File seems to be ok. The problem seems to be in displaying the
graph. Is there a way to debug this? There are no error messages in the
logfiles.
Try replacing "roomtemp" in hobbitserver.cfg with "Temperature".
I'm not sure if that makes a difference or not, though. Also, make sure
the script doesn't generate any other text besides "Temperature:
<value>"... I had a script that output some non-value text before the
actual text, which was causing NCV to try to parse that into a number
(and thus "NaN" - Not a Number).
Hi all,
I have just tried to set up a custom NCV graph to
monitor the room
temperature.
An external script generates a status page with the
following output
(example):
Temperature: 22.92
I have added the following entries to my
hobbitserver.cfg:
TEST2RRD="....,roomtemp=ncv"
NCV_roomtemp="Temperature:GAUGE"
GRAPHS="...,roomtemp,ncv"
My roomtemp.rrd File has been created and updates
regularly.
Output of rrdtool dump:
<rrd>
<version> 0001 </version>
<step> 300 </step> <!-- Seconds -->
<lastupdate> 1145970097 </lastupdate> <!--
2006-04-25 15:01:37
METDST -->
<ds>
<name> Temperature </name>
<type> GAUGE </type>
<minimal_heartbeat> 600
</minimal_heartbeat>
<min> 0.0000000000e+00 </min>
<max> NaN </max>
<!-- PDP Status -->
<last_ds> UNKN </last_ds>
<value> 2.1708600000e+03 </value>
<unknown_sec> 0 </unknown_sec>
</ds>
After that, I have added the following to my
hobbitgraph.cfg:
[roomtemp]
TITLE Server Room Temperature
YAXIS degrees
DEF:temp=roomtemp.rrd:Temperature:AVERAGE
LINE2:temp#FF0000:Room Temperature
COMMENT:\n
GPRINT:threads:LAST: \: %5.1lf (cur)
GPRINT:threads:MAX: \: %5.1lf (max)
GPRINT:threads:MIN: \: %5.1lf (min)
GPRINT:threads:AVERAGE: \: %5.1lf (avg)\n
There is no graph showing up on status page nor on the
trends page. On
the status page there is only a link "hobbit graph
ncv:roomtemp" and on
the trends page only a link "hobbit graph roomtemp".
What am I doing wrong? Do I have to configure other
things than these?
Thank you in advacne for answering.
Chris
To unsubscribe from the hobbit list, send an e-mail to
hobbit-unsubscribe at hswn.dk
More information about the Xymon
mailing list